Hi, I'd like to create a module with warning conditions. Is it possible to set more than one interval to warning condition? For example: I've got a module of temperature which is sending data of temp, like 90 °F. The module has to be in warning status if the temperature is less than 50 °F and also has to be in warning status if it is bigger than 120 °F. Best regards, gadge
module status interval
gadge · 31 mar 2017, 19:09 · 4 mensajes · 57 visitas
- Inicio del debate
Hello gadge, Yes, you can use the inverse interval feature of the thresholds. With this feature you would se the threshold, let's say from 50 to 120, in this case the module would go warning when retrieving values between 50 to 120, ok. If you enable the inverse interval, then the module will get warning status if the values are OUTSIDE of the specified interval, so, below 50 and above 120. So I think this feature is exactly what you need :) You can find additional information here: http://wiki.pandorafms.com/index.php?title=Pandora:Documentation\_en:Configuration#.28.3E.3D\_5.x.29\_module\_warning\_inverse\_.3Cvalue.3E This doc is for local modules (executed by software agents), but you can configure inverse interval on any module from the web console. Kind regards, Antonio.
Hi, I'm trying to figure out how to configure warning and critical conditions in both positive and negative ranges. For example, critical up to -10 or above 10 and warning up to -5 or above 5. Is this possible too with inverse interval? I suppose I would then configure critical from -10 to 10 and warning from -5 to 5, assuming critical takes precedence, right?
Hello Syranolic, Yes, that would work :). Kind regards, Antonio.